Q25
(a) In a series LCR circuit connected across an ac source of variable frequency, obtain the expression for its impedance and draw a plot showing its variation with frequency of the ac source.
(b) What is the phase difference between the voltages across inductor and the capacitor at resonance in the LCR circuit ?
(c) When an inductor is connected to 200 V dc voltage, a current of 1 A flows through it. When the same inductor is connected to a 200 V, 50 Hz ac source, only 0.5 A current flows. Explain, why ? Also, calculate the self inductance of the inductor.
OR
(a) Draw the diagram of a device which is used to decrease high ac voltage into a low ac voltage a
Solution
(a) Consider an alternating e.m.f. is connected in series with an inductor, resistance R and capacitance C. Let, E and I be the instantaneous values of e.m.f. and current in the LCR circuit VL, VC and VR be the instantaneous values of voltage across inductor, capacitor and resistor respectively. Then,
(b)At resonance,Xᴸ=Xc
iXᴸ=iXc
Vᴸ=Vc
The voltage across inductance and capacitance are equal and have a phase difference of 180° at resonance.
c) Since the reactance of an inductor is zero for d.c. circuit. But the inductor offers resistance to an a.c. circuit. Therefore, the current decreases for the same inductor when it is connected with an a.c. source.
When inductor is connected in a.c. circuit:
OR
(a) Step-down transformer:
It is a device used for converting high alternating voltage at low current into low alternating voltage at high current and vice-versa.The device works on the principle of mutual induction i.e., if the current or magnetic flux linked with a coil changes then an e.m.f. is induced in the other coil.
In step-down transfomer Np > Ns and transformation ratio is less than 1.
1. Copper losses: Due to resistance of winding’s in primary and secondary coils, some electrical energy is converted into heat energy.
2. Flux losses : Some of the flux produced in primary coil is not linked up with secondary coils.
3. Hysteresis losses : When the iron core is subjected to a cycle of magnetization the core
gets heated up due to hysteresis known as hysteresis loss.
4. Iron losses : The varying magnetic flux produces eddy current in the iron core, which leads to the wastage of energy in the form of heat.
(b) Length of wire line = 20 x 2 = 40 km
Power to be supplied = 1200 kW = 1200 × 10³ W
Voltage at which power supplied = 4000 V